• Some users have recently had their accounts hijacked. It seems that the now defunct EVGA forums might have compromised your password there and seems many are using the same PW here. We would suggest you UPDATE YOUR PASSWORD and TURN ON 2FA for your account here to further secure it. None of the compromised accounts had 2FA turned on.
    Once you have enabled 2FA, your account will be updated soon to show a badge, letting other members know that you use 2FA to protect your account. This should be beneficial for everyone that uses FSFT.

Ups suggestion

stone

n00b
Joined
Jul 22, 2004
Messages
57
Hi im looking for a ups for my system and need some ideas,spec as follow:

Dell 2005FPW
Logitech 2.1 Speakers
Logitech cordless desktop(mouse +keyb)
Usb 2.0 Ext. Hd
AMD x2 4400+
250gb Maxtor SAta
Nvidiad 7800gtx
Abit An8-Ultra
2x512mb ddr500 OCZ VX
PX-716A DVD-RW
Antec Smart Power 2.0 500W
 
I'd recommend APC, at least 500-600 VA, considering the processor and video card you have. APC has a UPS selector on their website that will help you choose the appropriate UPS. Second to APC, I'd go with tripplite.
 
a Liebert GXT2 1KVA


would be at the top of my list
a true online double inverted UPS
with plenty of run time for that config

only if Im not mistaken that Antec isnt active PFC
which leads to nonlinear load issues
(with a true online or a standby when on battery power)

UPS Nonlinear Loads

Most end users are oblivious to the problems encountered when an online UPS interacts with nonlinear load, such as a switchmode power supply. Fig. 3, on page 42, illustrates the interface between an online UPS and a switchmode power supply. The switchmode supply within the host system consumes its current in high amplitude pulses, and as a result overloads the UPS, distorts its output and degrades in performance. This isn't the case if the SMPS has power factor correction (PFC); and in the United States most SMPS don't have PFC.

Repeated measurements under practical conditions show that in non-PFC SMPS, the current peak to rms ratio reaches a crest factor in the range of 2.5 to 3.5. This high crest factor imposes a difficult load for the UPS.

Manufacturers specify UPS capacity in volt-amperes, and set the UPS current limit with resistive loading. This affects the user in two ways: first, the actual power (in watts) that the online UPS can deliver is 75% to 80% of its VA rating. Second, the UPS cannot support a nonlinear load like a SMPS to full power capacity. In fact, it can support an SMPS only rated to 30% to 40% of its capacity. A 1kVA online UPS will only be suitable for backing up a system energized by a 300W to 400W (non-PFC) switchmode power supply. Attempts to draw higher power by the SMPS will severely distort the output of the UPS and may result in shutdown. Some UPSs support nonlinear loads to various degrees, but the above rule is safe to use as a guideline.

The whole idea of generating a high-purity sinewave within the UPS, and then rectifying it within the SMPS is wasteful. A UPS may be deployed to run non-electronic loads, such as lights or motors. However, this is a minor portion of the market for online UPS. Many applications back up computers and telecom devices, as well as instrumentation systems used for critical applications. In all of these applications, the immediate load for the UPS is the SMPS within the systems. Peak current and inrush current are associated with this load at startup. This current of 40A to 80A per SMPS will cause the UPS to shutdown due to overloading, or the UPS must transfer the load to utility to draw its inrush.
 
As an eBay Associate, HardForum may earn from qualifying purchases.
Ice Czar said:
a Liebert GXT2 1KVA


would be at the top of my list
a true online double inverted UPS
with plenty of run time for that config

Good suggestion. I might need to pick one of those up myself...
 